yet we all use them because the inductance effect determines the corner speed of the motor, the speed where torque drops off, and a good mechanical design should never operate above the corner speed, at least not when cutting.
Yes, it's generally true and often much less in practice. But you do need enough bulk smoothing capacitance to cope with the occasional peak demand.
25A @ 30V AC will give you 25A @ 42V DC
.Last edited by irving2008; 29-10-2013 at 07:09 AM.
-
29-10-2013 #2
With my maximum of 24A (6 motors at 4A) should I go with 500VA or 630VA and what capacitance do I need for smoothing?
On the webpage of the toroid manufacturer the calculations are slightly different, and I'm a bit confused, probably I should ask them.
Full wave bridge (FWB) With capacitor:
VAC = 0.8 x ( VDC +2 )
IAC = 1.8 x IDC
WATTS = VDC x IDC (output)
VA = 1.4 x ( WATTS + 2 IDC* )
-
29-10-2013 #3
Those calcs are for steady state load and make assumptions about power factor etc. to limit core heating and losses. If you go that route you'll end up with a massively overspec'd, physically large and overpriced transformer.
Steppers are nothing like that, the duty cycle is nothing like steady state. I don't know why you have 6 motors but I'd be surprised if you need more than 60% of the total load and most of the peakiness is handled by the capacitors.
So use:
VAC = (VDC + 1.5)*0.7
IAC = IDC
VA = IAC * VAC, then chose next largest
for 2 parallel secondary windings each is rated at IAC/2
The 1.5 is voltage drop across rectifier, can be 1, 1.5 or 2 depending on product.
So 24A @ 60% = 15A approx. = IAC (or 2 windings @ 7.5A each)
VAC = (42+1.5)*0.7=30V
VA = 30*15=450 so use 500 or 625VA
-
29-10-2013 #4
Thread Information
Users Browsing this Thread
There are currently 1 users browsing this thread. (0 members and 1 guests)
Similar Threads
-
Toroidal Transformer
By Carlb1058 in forum General ElectronicsReplies: 7Last Post: 17-08-2013, 06:54 AM -
Stepper Drives
By GTJim in forum Marketplace DiscussionReplies: 4Last Post: 05-04-2013, 12:05 PM -
Nema 34 Stepper Drives,
By drumsticksplinter in forum Gantry/Router Machines & BuildingReplies: 7Last Post: 03-04-2013, 04:20 PM -
Toroidal transformer voltages - sanity check needed!
By m_c in forum General ElectronicsReplies: 16Last Post: 03-10-2011, 08:34 PM -
Contactor sizing?
By Swarfing in forum General ElectronicsReplies: 5Last Post: 27-12-2010, 08:58 PM




Reply With Quote

Bookmarks