    Quote Originally Posted by PAULRO View Post
    anyway, i tried as suggested Jazz and still no joy. I set PD001=1, PD002=1, disconnected the wires to relay 1 ( run/stop) and tested with meter , i then tried to trigger the relays alternating between M3 and M5 on the MDI window but the condition of relays never changed. however i can go to outputs tab and toggle the relays on/off and will get a result.
    How did you toggle it with the active state or the Enable.?

    The output Active state is not a Switch for toggling any thing On/OFF. It's a Logic condition that needs to be set so things can work correctly.
    The enable is just that.!! . .Your turning the output off. So if the relay changes state then you probably have the Wrong Active Logic set and relay is coming on straight away and by disabling the Output it gets turned off.!

    Set Active LO(unticked) and try M3/M5 again if relay doesn't change state(or Click) Set it HI(ticked) and try M3/M5 again.

    Don't go Chopping and changing settings all over the place as it really makes finding faults difficult. Only make one change then Test.

  2. The Following User Says Thank You to JAZZCNC For This Useful Post:


  3. #2
    i toggled the active state of the relays to see if mach3 could change the state of the relay from a non responsive state . i have them set back now to the folowing the run relay 1 is on constantly because of active high setting. if i input M3 the spindle will run at 250-300rpm . M5 stops the spindle again. the only relay to change state is the PWM dependant relay 3
    Attached Thumbnails Attached Thumbnails Click image for larger version. 

Name:	OUTPUT 27.png 
Views:	850 
Size:	16.4 KB 
ID:	15425  

  4. #3
    Paul your not listening properly because if you'd done as I suggested then the spindle wouldn't start at all. And the speed would be controlled from the VFD using what ever speed you set.

    You need to take a few steps back and deal with one problem at a time. Stop changing settings willy nilly because this makes the Job of helping so much harder. All this does is waste yours and my time by chasing false issues. I need you to only change one thing at a time then report what happens.

    First all you need to do is get Relay #1 working. Forget #2 & #3 we don't need them so you can turn them off on the BOB and disable them in Mach3.

    Straight away I see that you have the Wrong Pin number set for Relay #1. It should be Pin 16 not 14.
    Pin 14 is for the PWM Speed control which I believe is working fine just needs setting up for correct speeds which can be done later. NOT NOW.!!

    So to re cap Tell me which terminals your connecting to on the Relay.
    Set Output #1 = pin16 Active LO.
    Turn off the Enable for Outputs #2, #3.


    Next the relay will have 3 terminals which are you connecting to.?

  5. The Following User Says Thank You to JAZZCNC For This Useful Post:


  6. #4
    i have relay 1( OUTPUT 1)
    set to pin 16, active LO. ( ticked) ( all other relays disabled. )
    TERMINALS on relay
    N.O CONTACT =FOR on VFD
    COMMON= DCM on VFD
    Last edited by PAULRO; 26-05-2015 at 08:28 PM.

  7. #5
    RELAY 1 is on . i metered accross the N.O contact and common and have continuity.

  8. #6
    Quote Originally Posted by PAULRO View Post
    RELAY 1 is on . i metered accross the N.O contact and common and have continuity.
    Ok well first makes sure Spindle is OFF. Type M5 in MDI. Check Continuity again.
    If still got continiuty then Change active state (NO Tick) and Check continuity again. It should drop Off. Type M3 and it should give continiuty again.
    If it does you are working correctly.
    Last edited by JAZZCNC; 26-05-2015 at 08:38 PM.

  9. The Following User Says Thank You to JAZZCNC For This Useful Post:


  10. #7
    that's O.K. Relay turns on/off using M3/M5. i had to change active lo setting to set it correct way .

  11. #8
    On the side topic of pumps - I use a similar Whale pump. I use 12V to run it for a few seconds to purge bubbles more quickly, but I then run it on 5V. Seems to circulate enough water to keep the spindle cool, and I have run it like that for quite a few 5-6hr sessions continuously with no apparent ill effects.

    Good luck with the Mach3/BOB issues!

  12. The Following User Says Thank You to Neale For This Useful Post:


  13. #9
    hi Neale, how do you control the 12 volt psu dropping out and the 5 volt kicking in?

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. NEW MEMBER: Hello everyone. Total newbie here. Where do I begin?
    By DarkWalkJRB in forum New Member Introductions
    Replies: 2
    Last Post: 07-02-2012, 08:31 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •