Thread: Ground loops and earthing
Threaded View
-
03-07-2014 #3
Ok common misunderstanding Here.? Your mixing up AC Earth and DC negative. They are very differant and should not be mixed up.
Your BOB will be DC and the Charger is converting AC to DC so your Phone charger is the only thing that should be connecting to EARTH not the BOB.(If charger as Earth often Don't)
Same goes with Other DC powered components IE: Drives etc. Only the Earth of the supplying Transformer should go to the Star EARTH point. Any DC Negatives should go to the (-) of the DC side of the supply.
One end of shields for things like Steppers, Limits, Homes etc go to the Star EARTH point. The spindle cable from VFD to spindle is the Only exception and can be connected at both ends and then it's best to run it back to Earth point on VFD. If the VFD is then powered from same AC supply in control box then run it's earth to the Star EARTH point.
Run Machine frame Earth back to Star EARTH point. Don't Earth the PC case and best to run it from separate supply to Control box.Last edited by JAZZCNC; 03-07-2014 at 01:10 AM.
Thread Information
Users Browsing this Thread
There are currently 1 users browsing this thread. (0 members and 1 guests)
Similar Threads
-
Earthing?
By manofgresley in forum General ElectronicsReplies: 70Last Post: 29-03-2018, 11:56 PM -
Laser Machine Grounding/Earthing
By Want2build1 in forum Laser Machines & BuildingReplies: 31Last Post: 09-02-2015, 10:18 PM -
threading ground bar ends
By dazza in forum Metalwork DiscussionReplies: 39Last Post: 11-02-2014, 11:41 PM -
FOR SALE: Strong steel welded base with ground flat surface.
By black5f in forum Items For SaleReplies: 0Last Post: 14-01-2012, 07:20 PM -
RFQ: Precision Turned/Ground parts
By Jimmybristol in forum Projects, Jobs & RequestsReplies: 0Last Post: 08-01-2011, 04:12 PM
Bookmarks