  1. #1
    I think it would be good if you put a schematic up exactly how you have wired it. Is that a RCD on the main fuse? If you have blown the 13A fuse you may have an earth fault. Is there a reason you are using an SCR in the circuit? What type of MCB have you used ie B type etc? ..Clive

  2. #2
    As Clive said, a diagram would be best. However I'll risk guessing - if you're connecting the transformer to the mains without a soft start socket, then the inrush current from charging the capacitors may be too high. Also, are those automotive type blade fuses and are they used on the mains or 70V circuit? If so you shouldn't use that type there as they're only rated for 12-24V. To be fair the fuse still seems to have worked... but that's maybe not the point!
    Old router build log here. New router build log here. Lathe build log here.
    Electric motorbike project here.

  3. #3
    I'm not an expert on electrics but I wouldn't use the automotive fuse on mains AC. Either MCB or DIN mounted glass fuse holder designed for AC would be my choice.

    I did a lot of looking into fuses for the DC side and concluded that it was ok to use a 5A 12V automotive blade fuse at 5A 70V because the fuse would blow at a certain power which is the current squared times the fuse resistance. The voltage didn't come into it until the fuse blew and the gap created needed to be big enough to prevent an arc ( therefore still allowing current through).

    That was where I got to it anyway. I also saw Irving use one ( with a disclaimer)!

    Clive - you wrote SCR did you mean SSR as in solid state relay?
    Last edited by routercnc; 08-04-2015 at 10:28 PM.
    Building a CNC machine to make a better one since 2010 . . .
    MK1 (1st photo), MK2, MK3, MK4

  4. #4
    Rich's Avatar
    Lives in Warrington, United Kingdom. Last Activity: 08-04-2015 Has been a member for 9-10 years. Has a total post count of 30. Received thanks 1 times, giving thanks to others 0 times.
    Thank you all, I can see I've made a mistake by using a spade as a primary fuse. The intention was to use a slow blow fuse, per the thread. I have one ... but because it wasn't on the purchase list, it dropped off the build list.

    I will draw a schematic and add a parts list, that will help clarify my issue and hopefully put me back on track.

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. Reducing 12v DC to 0.5V DC no more than 1A draw
    By AdCNC in forum General Electronics
    Replies: 18
    Last Post: 31-12-2022, 08:14 PM
  2. Reducing costs
    By tonygagey in forum Gantry/Router Machines & Building
    Replies: 16
    Last Post: 13-08-2014, 11:33 AM
  3. How I almost set fire to my garage...
    By cncJim in forum General Discussion
    Replies: 26
    Last Post: 07-02-2014, 11:51 AM
  4. shed/garage electronics,
    By jcb121 in forum General Electronics
    Replies: 12
    Last Post: 29-07-2013, 10:52 AM
  5. My garage
    By wilfy in forum Workshop & Equipment
    Replies: 55
    Last Post: 18-02-2013, 06:40 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •