Thread: Soft Start Advice
Threaded View
-
31-01-2014 #1
I need a bit of advice as I’m getting slightly confused.
As you can see from the sketch below I want to include a basic soft start circuit into my control panel, but I have the main toroidal transformer, a 24 volt power supply and a 5 volt power supply.
If I ignore the 24v and 5v power supplies for now, I calculated the resistor required as HS50 33R. From the following:
I = VA / V
I = 750 / 230 = 3.26 amps
With a limit of 200% of the power current = 6.52 amps
R = V / I
R = 230 / 6.52 = 35.28 ohms
As I need both the 24 and 12 volt supplies, my questions are:
- Should I connect them up as shown, after the soft start or after the safety relay?
- Do I need to include the additional power supplies in the calc for a suitable resistor, and if so how?
- The HS50 refers to watts, I have only used this as it has been suggested in an article I read. Is this correct?
- I am hoping to find a suitable relay with a timer, can anyone point me in the right direction?
Regards,
Jim
Thread Information
Users Browsing this Thread
There are currently 2 users browsing this thread. (0 members and 2 guests)
Similar Threads
-
Opensource machine for dedicated soft tooling?
By gavztheouch in forum Moulding MachinesReplies: 3Last Post: 10-02-2014, 10:27 PM -
RFQ: Panels cut from soft plywood
By Rockeyes in forum Projects, Jobs & RequestsReplies: 0Last Post: 12-04-2013, 04:38 AM -
Where to start?
By Inquisitor in forum Gantry/Router Machines & BuildingReplies: 7Last Post: 27-11-2012, 02:35 PM -
is this 2.5d where do i start? help please if you can
By h4ppy-chris in forum General DiscussionReplies: 4Last Post: 29-03-2011, 12:21 PM -
Scrool jaw ring for hydraulic soft jaws.
By Pmac in forum Tool & Tooling TechnologyReplies: 4Last Post: 28-01-2010, 07:55 PM
Bookmarks