Ding Dong Ding Dong.!! . . . . 24Vdc is correct for these drives Clive they only Take 30Vdc Max so don't want to release the Magic smoke.!!
Ok well see a couple of things.
Don't see the latching Relay wiring.?
Don't see the point of the Green 240V Led just use Red Led that's on all the time Power is On. Use the Green Led for indicating System is Reset and Ready. I'd Also use 24V leds.
Don't Like the fact your using 1x Mcb for 3 x Psu all different sizes. You will be better having the smaller ones on separate Glass Din rail fuses.Last edited by JAZZCNC; 06-04-2015 at 09:55 AM.
-
06-04-2015 #2
ill upgrade to real drivers one day :), regarding the other PSU's the 9v powers the USB controller, and the 12v spins some fans on the drivers and the din 24v powers the estop thingy to kill power to the other psu's
-
06-04-2015 #3Yes I had checked that out in the early post. I was just saying its a shame to use such low voltage drivers. ..CliveDing Dong Ding Dong.!! . . . . 24Vdc is correct for these drives Clive they only Take 30Vdc Max so don't want to release the Magic smoke.!!
-
07-04-2015 #4
OK updated to V3 now and I have added the e-stop / latch relay connections? removed the 9v and 12v PSU to avoid confusion at this point and ill upgrade the fans to 24v and run off the Din Rail PSU. Am i close correct with the relay / contactor connections?
Thanks againLast edited by Dwayne Dibbley; 09-04-2015 at 07:43 PM.
-
10-04-2015 #5
Ive attached a schematic of what i think the latch circuit looks like:
S1 = Go push button NO
S2 = E-Stop NC
S3 = Stop Button NC
RY1 = double pole latch relay NO ( can you also do the same with a single pole? )
RY2 = contractor DC coil
Thanks
-
10-04-2015 #6
Surly a stop button should not be the same as E-stop. ..Clive
-
10-04-2015 #7
-
10-04-2015 #8
When you press E-stop or the stop button then latch is dropped because power is removed from relay. So in your schematic E-stop and Stop are the same.
Same in Mach3 if you press Stop while machine is moving then consider it just the same as pressing E-stop button. You will lose position and need to Re-home before continuing. Only Feedhold is safe controlled stop.
Thread Information
Users Browsing this Thread
There are currently 3 users browsing this thread. (0 members and 3 guests)
Similar Threads
-
What gauge wire for motors and drivers etc?
By glynster in forum Gantry/Router Machines & BuildingReplies: 8Last Post: 01-03-2015, 01:40 PM -
Mach 3 control panel help
By IanParkin in forum Artsoft Mach (3 & 4)Replies: 19Last Post: 05-09-2014, 04:05 PM -
VFD to motor cable wire size (Gauge)
By artman12us in forum Spindles & Drive MotorsReplies: 2Last Post: 24-04-2014, 07:11 PM -
RFQ: Aluminium Control Panel
By m_c in forum Projects, Jobs & RequestsReplies: 5Last Post: 27-04-2013, 08:46 PM -
30 gauge solid core insulated wire
By Wobblybootie in forum General DiscussionReplies: 8Last Post: 23-06-2010, 10:17 PM




Reply With Quote

Bookmarks