Quote Originally Posted by Clive S View Post
Neutral is not earth In the UK the earth is bonded to the neutral in most cases but not always.
The ground in your case is a central point where all the screens and ground are connected together in one place (star point) and that point in connected to the general earth connection. This is to try and stop ground loops. ..Clive
Ah, sorry, mistook 'star point' as the star of a 3 phase system which is commonly earthed. Thanks, understood what you explained.

Out of interest, my drawings show the encoder shield only being attached on side and from speaking to a colleague this morning, that seems common practice (not to earth both sides of a shield). Would that be correct based on the collective experience here?