17-01-2016 #6
Ok well you can only have one or the other control the Contactor other wise you defeat the point of HVEnable. The point of HV is speed so no point having the Safety relay tell Controller E-stop happened then HV shut down contactor because it's actually longer.
So the Answer is you control Both directly with E-stop using two contacts on the E-stop.
One Contact controls the Master safety Relay which you then use for System Reset and any other things you want to Kill power to like, Vacuum, Coolant etc etc.
Then have the other contact control the E-stop INPUT which then Controls HV OUTPUT and Contactor which turns on Main Drives PSU.
This way you still have Safety Relay in charge of Reset system but with the faster HV in charge of the Drives power. The HV will only turn them ON when Mach is Reset. The system Reset will only turn on Safety Relay when E-stop is clear so the System will re-set and at same time E-stop Input on controller is clear so HV is safe to turn On when Mach is Reset.
Hope this makes sense.!!
Edit: If you want double safety run the HV Output wire thru the Safety relay Contact before going to Contactor. This way if Safety relay fails the PSU will lose power.Last edited by JAZZCNC; 17-01-2016 at 11:40 AM.
Thread Information
Users Browsing this Thread
There are currently 1 users browsing this thread. (0 members and 1 guests)
Similar Threads
-
Electric motorbike racing
By Jonathan in forum General DiscussionReplies: 46Last Post: 16-08-2016, 03:28 PM -
PSU Assistance
By CNCStudent in forum General ElectronicsReplies: 13Last Post: 05-08-2015, 07:07 PM -
FOR SALE: 240v decent electric filter
By DrNik in forum Items For SaleReplies: 3Last Post: 16-03-2015, 12:30 PM -
ES-D1008 + CSMIO/IP-S wiring
By Matt81 in forum CS-Lab (CSMIO)Replies: 3Last Post: 03-05-2014, 10:56 PM -
NEW MEMBER: Tunisien request for assistance
By ali hedi in forum New Member IntroductionsReplies: 0Last Post: 01-06-2009, 05:37 PM
Bookmarks