    Use a separate Relay and have the VFD fault Signal turn it on when goes active. Run the E-stop signal thru NO contact.
  2. The Following User Says Thank You to JAZZCNC For This Useful Post:
  3. #2
    new small issue/confirmation : regarding ground, it is best to have one point for all ground right? meaning if chassis of one device is grounded and the whole sheet is grounded, I should not wire the ground connections of other devices if they also ground their chassis right?
    illustration:
ID:	17269Click image for larger version.
    in first photo you can see I have connected the power supply chassis to ground wire which goes back to main ground point ( distribution terminals ) so the whole back is grounded. in second photo VFD and power line filter have earth connections but by checking continuity test already these points are connected to back also. so should I skip connecting ground wire to them?
    thank you!
    after some research I realized that all ground contacts should be connected and not rely back panel, anyway I need confirmation of another issue please
    when connecting the VFD with contactor, should all wires ( L,N,Gnd) be connected through the poles or can I just connect the Live with contactor and rest direct from mains power?
    what about the DC output power supply for the drivers?
    thanks!
  5. #4
    Quote Originally Posted by Noplace View Post
    thanks!
    If you really want to connect the VFD through the contactor then just the live would be fine (and not the N or E), but having said that I suppose it depends on the power system to your building as it may be different than the UK.
    I personally would not connect the mains VFD through the contactor but would just connect the signal wire to make it stop.
    The DC output from the power supply should not go through the contactor either .
    Perhaps you should find somebody local to give you some help with this before you get a chance to damage it all or yourself.
  7. #5
    hmm well I seem to remember reading that it's safest to turn off power instead of just relying on signal coming out of the devices(drivers,VFDs)
    and the examples in the CSMIO show it this way.
    also I would like to you utilise the software to enable a power on signal
  8. #6
    If you still want to include a contactor to the VFD, then I'm pretty sure that if you hit the e-stop (and turn off the mains power to the VFD) it will not like having the spindle spool down and feeding power back into it when it is not on. Would it damage it? Not sure. But I wouldn't risk it myself.
    I see in one of your earlier posts that you have a braking resistor, which can allow quicker ramp downs (although I've not used mine as it is plenty quick enough without). If you plan to use it I would imagine that killing the power to the VFD would not allow it to use the resistor and it would coast down over a much longer period.
    So if you still want to do this I think you would need a delayed timer on the contactor to switch it off after say 5 seconds, depending on your ramp down parameters. This adds complication, but I know Dean has done this so it is possible. This is in addition to the e-stop logic signal telling the VFD to stop, which you would do first to stop the spindle safely under VFD control.
    I seem to remember reading some time ago that you can be specific and tell the VFD that this is an emergency (not just a regular stop / start command) and it will do an emergency ramp down / stop which is quicker.
  9. The Following User Says Thank You to routercnc For This Useful Post:
  10. #7
    If your refereing to HV enable then it's not really very suited to this application because it will Kill power to VFD every time you put Mach in reset. Which will be often. This constant stop starting isn't good for the Vfd and will damage it over time.
    Also you won't be able to start cutting straight away after a reset and will need to wait for VFD to power up fully which could be pain.
    If you really do want the VFD turned off then I would have the VFD tied to E-stop but keep it separate from HV enable. Just have HV enable control the drives PSU and the Spindle RUN Command.
    This way when Mach3 is in Reset mode then the VFD stays on but can't started until mach is reset. At which point HV enable turns on the drives and allows spindle RUN signal to reach VFD when needed.
    Think of it has two separate systems working together. E-stop is hardwired and kills everything, HV enable just kills Drives and Run etc but only when mach is in Reset.
    There are many times you'll want some things powered while Mach is in Reset mode. Ie Vacume but at same time your not in E-stop condition.
  11. The Following User Says Thank You to JAZZCNC For This Useful Post:
  12. #8
    thank you guys for the insight and preventing me from making a mistake, I guess the VFD manual confused me because it has some notes about when using a contactor. so in this case is there use for a contactor (for the VFD) at all if controlled through a constant turn on signal?
  1. Electric motorbike racing
    By Jonathan in forum General Discussion
    Last Post: 16-08-2016, 03:28 PM
  2. PSU Assistance
    By CNCStudent in forum General Electronics
    Last Post: 05-08-2015, 07:07 PM
  3. FOR SALE: 240v decent electric filter
    By DrNik in forum Items For Sale
    Last Post: 16-03-2015, 12:30 PM
  4. ES-D1008 + CSMIO/IP-S wiring
    By Matt81 in forum CS-Lab (CSMIO)
    Last Post: 03-05-2014, 10:56 PM
  5. NEW MEMBER: Tunisien request for assistance
    By ali hedi in forum New Member Introductions
    Last Post: 01-06-2009, 05:37 PM