26-05-2016 #9
OK, to clarify:
Cg represents the derating factor for grouping cables.
A cable with a current rating of 6 amp installed in trunking alongside other circuits, that's circuits not cables!, would now have a Cg value, the Cg value is 0.57.
This means the cable current rating becomes: 6 x 0.57, that's 3.42 amp.
To add to this, you should note that the grouping factors are based on assumption, the assumption that all of the cables in the group are carrying their rated current.
So, if however a cable is not going to be carrying more than 30% of its grouped current rating, that cable can actually be omitted from the group rating calculation...
...an example, if you've got lets say 6 circuits in a group of cables but 1 of those cables is known to be operating below the said 30% consistently, you can safely calculate the group on the basis that it only consists of 5 circuits.
Here are some correction factors for multicore cable:
OK Clive, how did I do?
.MeLast edited by Lee Roberts; 26-05-2016 at 10:50 AM.
.Me
-
The Following User Says Thank You to Lee Roberts For This Useful Post:
Thread Information
Users Browsing this Thread
There are currently 1 users browsing this thread. (0 members and 1 guests)
Similar Threads
-
1.5 kw Chinese spindle cable
By 142victoria in forum Generic Chinese SpindlesReplies: 4Last Post: 02-11-2015, 09:53 AM -
motor and spindle cable size?
By paulus.v in forum General ElectronicsReplies: 4Last Post: 04-02-2014, 10:18 PM -
Ballscrew Thickness!
By AdCNC in forum Lead Screws, Nuts & SupportsReplies: 51Last Post: 03-02-2014, 06:01 AM -
Adding earth cable to 2.2Kw Chinese Spindle
By Dwayne Dibbley in forum Generic Chinese SpindlesReplies: 4Last Post: 13-03-2013, 04:04 PM -
VFD Cable and 2.2kw spindle wiring
By Flamered in forum Spindles & Drive MotorsReplies: 7Last Post: 24-08-2012, 07:29 PM
Bookmarks