    Quote Originally Posted by Clive S View Post
    Lee that is helpful but the chart does not show if the cables are in free space or bunched together in one sleeve as the cable will have to be derated when bunched because of heat build up.

    Edit Lee the Watts to Amps conversion has to state the voltage I know you have it done at 230V
    OK, to clarify:

    Cg represents the derating factor for grouping cables.

    A cable with a current rating of 6 amp installed in trunking alongside other circuits, that's circuits not cables!, would now have a Cg value, the Cg value is 0.57.

    This means the cable current rating becomes: 6 x 0.57, that's 3.42 amp.

    To add to this, you should note that the grouping factors are based on assumption, the assumption that all of the cables in the group are carrying their rated current.

    So, if however a cable is not going to be carrying more than 30% of its grouped current rating, that cable can actually be omitted from the group rating calculation...

    ...an example, if you've got lets say 6 circuits in a group of cables but 1 of those cables is known to be operating below the said 30% consistently, you can safely calculate the group on the basis that it only consists of 5 circuits.

    Here are some correction factors for multicore cable:




    OK Clive, how did I do?

    .Me
    Last edited by Lee Roberts; 26-05-2016 at 10:50 AM.
    .Me

  2. The Following User Says Thank You to Lee Roberts For This Useful Post:


  3. #2
    OK Clive, how did I do?
    Fine Lee I was not taking the p#'@s I just thought that the Voltage had to be added etc for the sake of people with no knowledge of sparky stuff.
    ..Clive
    The more you know, The better you know, How little you know

  4. #3
    Quote Originally Posted by Clive S View Post
    Fine Lee I was not taking the p#'@s I just thought that the Voltage had to be added etc for the sake of people with no knowledge of sparky stuff.
    I know mate :), I was only having fun, my ask of "how i did" was actually sincere as I only know what I've learnt in an unformal way, im no professional.

    At the same time I thought it was a good cue for providing the knowledge, as like you say those conversions need to take the operating voltage into consideration if starting from the beginning and doing your own calculations.

    .Me
    .Me

Thread Information

Users Browsing this Thread

There are currently 4 users browsing this thread. (0 members and 4 guests)

Similar Threads

  1. 1.5 kw Chinese spindle cable
    By 142victoria in forum Generic Chinese Spindles
    Replies: 4
    Last Post: 02-11-2015, 09:53 AM
  2. motor and spindle cable size?
    By paulus.v in forum General Electronics
    Replies: 4
    Last Post: 04-02-2014, 10:18 PM
  3. Ballscrew Thickness!
    By AdCNC in forum Lead Screws, Nuts & Supports
    Replies: 51
    Last Post: 03-02-2014, 06:01 AM
  4. Adding earth cable to 2.2Kw Chinese Spindle
    By Dwayne Dibbley in forum Generic Chinese Spindles
    Replies: 4
    Last Post: 13-03-2013, 04:04 PM
  5. VFD Cable and 2.2kw spindle wiring
    By Flamered in forum Spindles & Drive Motors
    Replies: 7
    Last Post: 24-08-2012, 07:29 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •