    I am not surprised that you have emf problems I think I would remove the vfd from the control box plus sort out the rats nest of wires try to keep or the signal wires away from the power wires and avoid running them side by side.

    If you have to cross power wires do so at 90' if possible. Have you connected all the screens to one star point? I don't think it helps having the PP ribbon cable I would try and replace that by connecting the PP cable from the PC direct to the BOB without the ribbon cable.

    You have the basis of a good control box but you have not made the best use of the cable management in there.

    edit: Is that a plastic control box? have you mounted everything on to a backplane (ie metal plate) I think one of your main problems will incorrect grounding
    Last edited by Clive S; 06-03-2016 at 11:52 AM. Reason: add text
    ..Clive
    The more you know, The better you know, How little you know

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. Noise, Interference, and unexplained electrical behaviour
    By g4ghp in forum General Electronics
    Replies: 4
    Last Post: 24-04-2014, 11:39 AM
  2. Bearing interference fit / press fit
    By Mad Professor in forum General Discussion
    Replies: 5
    Last Post: 30-09-2012, 11:26 PM
  3. 19inch Rack Enclosure - interference?
    By Washout in forum General Electronics
    Replies: 12
    Last Post: 22-09-2012, 09:10 PM
  4. Problem with X
    By gorbo in forum General Discussion
    Replies: 17
    Last Post: 24-02-2011, 05:33 AM
  5. Z Problem
    By airwolf in forum Machine Discussion
    Replies: 2
    Last Post: 10-11-2009, 08:08 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •