Hi Clive

Thanks for the note. In the instruction manual the recommended wire gauge is 5.3mm² with 30 amp fuses, seems a bit heavy if you ask me. If anyone has any ideas i'm all ears.
Cheers

Andrew
Quote Originally Posted by Clive S View Post
Andrew First welcome to the forum.

Re your VFD 2.2Kw at 220V is about 10A at full load which you will hardly ever use the majority of people on here I suggest will be using a standard 13A plug and if it is a short run from the vfd to the socket then 1.5mm cable will be fine.