IMO JAGUAR VFD help needed
Attachment 8729
Hi everybody!
I encounter a little problem operating my Denford Orac lathe with the IMO JAGUAR VC150 VFD.
I wanted to use the IMO VC150 in place of the Parajust because the last one lacks the capability for reversing.
The case here is, that the Parajust uses a 5k frequency control pot and the IMO VC150 uses a 10k pot. This means the Orac controller when applying the highest impendance for bringing the motor to a full stop. This will not happen and the motor is going to continue running at aprox. 300RPM because 5k is not enough for the IMO to completely cut the power to the spindle motor.
Also, the IMO was not fitted with a latching relay for start/stop control and the normally open momentary switch is not suitable for the IMO as is with the Parajust to activate this control.
If someone of you gents is familiar with the IMO JAGUAR VFD and successfully has made a similar modification using this inverter his advise on how one may overcome this different control impendance problem is highly appreciated.
cheers
Asto
-
Re: IMO JAGUAR VFD help needed
Would it not have been easier to keep the original drive but reverse the motor by using relays or contactors to swap the motor phases?
As for the new drive, you should be able to set its parameters to take a 0-5V or 0-10V input signal from the pot (assuming that the 5K pot outputs 0-5V?). For the latching circuit, there should be a way to set that on the drive but you might need a linking wire somewhere in the start/stop/run terminals. Otherwise, you'll have to latch a relay instead.
-
Re: IMO JAGUAR VFD help needed
Hi and thanks for the response.
Well, the original VFD I accidentally damaged. Its power module...a Gentron Powertherm B412F needs replacement but I have not managed to locate one yet.
On the other hand, in order to set parameters for the IMO I need the user manual for VC150 and this is something really rare to find today.
That's why i asked for help.
Parajust pot outputs 0-10 volts thats the only thing i know.
-
Re: IMO JAGUAR VFD help needed
0-10V is the standard signal, so that's good news. Bad news is that you're gonna need a manual for that drive in order to set it up properly. You'll probably find that the manual for ANY if the IMO Jaguar range will be OK as they standardise on parameter numbers and functions and the start/stop/run/speed/etc terminal connections will be the same.
Maybe one of these? Power Drive Services - Electric Motor Specialists - Fuji Manuals
-
Re: IMO JAGUAR VFD help needed
-
Re: IMO JAGUAR VFD help needed
This should be the same even though a different name on the unit
http://www.inverter.co.uk/applicatio...ini-manual.pdf
-
Re: IMO JAGUAR VFD help needed
Damn it, I've somehow ended up on eBay looking at Jaguar XKR's and XF's. I hate this forum. :)
-
Re: IMO JAGUAR VFD help needed
Quote:
Originally Posted by
birchy
Damn it, I've somehow ended up on eBay looking at Jaguar XKR's and XF's. I hate this forum. :)
Keep looking at XKR's, they are just beautiful!! (biased again as I have a pacific blue convertible). G.
-
Re: IMO JAGUAR VFD help needed
CUB - Drives Direct
http://www.drivesdirect.co.uk/Downlo...B%20Manual.pdf
this is the manual i had with my imo vfd
-
Re: IMO JAGUAR VFD help needed
Quote:
Originally Posted by
irving2008
Thanks Irving!
Though mine is VC150.
Swarfing there must be some problem with this link. Could not open the Pdf.
-
Re: IMO JAGUAR VFD help needed
Asto should not make a lot of difference, most of the connections and settings are the same across a lot of the different models. You have enough manuals here now to what you need. the only difference will be the frequency settings for the speed control which won't be hard to deal with. Post a pic of the one you have.
Also i think the VC150 = Cub 1.5 amp version
-
Re: IMO JAGUAR VFD help needed
Sure i will do that tomorrow
Thank you all
regards
-
Re: IMO JAGUAR VFD help needed
@swarfing Exactly so, I thought the Cub is the VC150 (except its not 1.5A but 1.5kW (2HP) LOL), IMO branded differently for different markets...
-
Re: IMO JAGUAR VFD help needed
Yes it is the 1.5kw Irving looking again. all config is the same as far as i can see on them all.
Paul
-
8 Attachment(s)
Re: IMO JAGUAR VFD help needed
Quote:
Originally Posted by
Swarfing
Yes it is the 1.5kw Irving looking again. all config is the same as far as i can see on them all.
Paul
Attachment 8739Attachment 8740Attachment 8741Attachment 8742Attachment 8743Attachment 8744
I hope these IMO images have a lot to say.
The schematic came out of the Parajust manual. The pdf extracts are for the Parajust
As you all see, control impendance is double in the IMO as Parajust needs 5K pot in order to bring the motor to full stop.
Attachment 8745Attachment 8746
-
Re: IMO JAGUAR VFD help needed
Ok this is much older than what we have been looking at. But you have all the information to connect this up so don't understand your problem with it Asto? Swap the potentiometer out for a 10k one
-
Re: IMO JAGUAR VFD help needed
You mean an external pot?
With an external linear rotary pot of 10K runs fine.I've done this already.
My problem is, that I totally disregard which way to proceed in order to alter settings that will cause the IMO find sufficient the Orac's 5K digital pot and bring the motor to a complete stop...Cause, when I deccelarate through the machines (-) button the control outputs a maximum 5K resistance. I really do not know if it is possible to alter this value to 10K.
-
Re: IMO JAGUAR VFD help needed
Maybe i am not understanding this completely. The wiring in the Orac should go directly to the VFD for the spindle control yes? or is it going by a different circuit first? Is the speed adjust from the software of the machine or just analogue control?
-
Re: IMO JAGUAR VFD help needed
That's right Swarfing.
The Orac's controller decides what resistance value to apply at the inverter input. And is wired directly to it even though the VFD may be removed and operate as stand alone to control motors of some other system.
Even when the machine is at manual mode the controller does the accel/deccel i guess by digitally switching resistors internally. It has to be this way how else would it be!
Is that the question or I have missed something due to the foreign language factor which applies for me here.
-
Re: IMO JAGUAR VFD help needed
Ok i understand now thank you. Does the machine speed controls ramp up and down linear or are there distinct steps in the ramping?
My thoughts were that the speed pot from the VFD ran directly to the machine controls. I do not know this machine and find it difficult without seeing it. Could you do a pic where the wires go from the VFD to the machine controls?
-
Re: IMO JAGUAR VFD help needed
...pics are on the way. Please wait a few minutes
-
Re: IMO JAGUAR VFD help needed
Well I guess the value we need to know is what voltage range the Orac controller outputs. It sounds like it might be 0-5v rather than 0-10v? At the end of the day, it's just a potential divider circuit, so it should be possible to configure the drive to accept the input and/or use some resistors to bring it within range.
-
Re: IMO JAGUAR VFD help needed
Same thoughts Birchy, wondering though if there is output adjustment on the Orac control circuit? if works on step ramp up then it must have fixed voltage divisions. A bit frustrating when the problem is not sat in front of you though?
-
3 Attachment(s)
Re: IMO JAGUAR VFD help needed
Attachment 8752Attachment 8753
The 2 wires coming out from the Orac's controller (last 2 connectors to the right circled by the yellow line) connect to No. 1-2-3 IN-terminals of the Parajust VFD and these 3 terminals are also circled by yellow line. The third wire is the Shield connected only to the VFD side> Strange but this is how the machine operated all these years.2 wire ends at the controller side but 3 on the vfd sideAttachment 8754
These three terminals are clearly shown on the attached original Parajust schematic.
K1 is a latching relay fitted on the original machine inverter (that with the large blue capacitor) which makes start/stop easy using just one normally open momentary switch.
so far I have not cleared in my mind how IMO JAGUAR fulfills the requirements for this function. Obviously it is designed a bit differently for start/stop control.This is another problem which I am about to encounter using the IMO in place of the Parajust.
-
Re: IMO JAGUAR VFD help needed
Mmmm i wondering if the Orac is using voltage control for the speed adjustment (10v?). the third wire is to ground the shielding of the cable, if it was connected both ends it could cause a ground loop that would cause interference so that is quite normal. Can you check the terminals of the Orac for voltage whilst adjusting the speed controls?
-
Re: IMO JAGUAR VFD help needed
...I've done this before and I know from the user manual that for speed control voltage is applied from 0-10Vdc. According to the that inverter specs one can accelarate or deccelarate even by applying an external variable 0-10V source between terminals 4 and 2 of TB! terminal block 4 being negative and of max. 500ma. This is where the wire shield goes.
For Start/stop control it uses 6Vdc
-
Re: IMO JAGUAR VFD help needed
Swarfing, the manual extract you see on previous page here explains all this. Just give it a glance if you please
-
Re: IMO JAGUAR VFD help needed
Thanks Birchy for the response.
Your idea of applying additional resistors to the network came to my mind as well. But then maybe it won't accelerate to max. RPM . What do you think?
-
Re: IMO JAGUAR VFD help needed
I've seen many of these oracs, and you're quite lucky just to have the inverter fail. In light of the age i would just bin the original controller and go to mach3.
-
Re: IMO JAGUAR VFD help needed
I guess the easiest solution might be a digital potentiometer? It takes a voltage input which controls the passive potentiometer.
Using an Analog Voltage to Control a Digital Potentiometer - Application Note - Maxim
-
Re: IMO JAGUAR VFD help needed
Quote:
Originally Posted by
i2i
I've seen many of these oracs, and you're quite lucky just to have the inverter fail. In light of the age i would just bin the original controller and go to mach3.
TBH, I was also thinking that the machine needs a complete upgrade, particularly given the age and likelihood of capacitors being dried up. But then I figured that either money is very tight or this is some sort of retro build. If the budget is tight, then LinuxCNC on an old PC might be a better option.
-
Re: IMO JAGUAR VFD help needed
Checked for voltage ...Stable 0.65 volts no change when trying to accelarate
-
Re: IMO JAGUAR VFD help needed
Now I understand what you mean Birchy.
But at the moment I am not getting any voltage measurements at the machine speed control output
Maybe there is some fault there.
-
Re: IMO JAGUAR VFD help needed
Yes, if it is a constant 0.65V throughout the selected speed range, then something is wrong. If that's the case, then maybe your original Parajust drive is OK but your CNC control is faulty?
-
Re: IMO JAGUAR VFD help needed
This is quite probable? Is there anybody else here that can check against theirs?
-
2 Attachment(s)
Re: IMO JAGUAR VFD help needed
Thank you both.
I am reading the Parker manual and it says ...\for Fast rotation requires pin 20 of 32 Pin input socket of SD2 drive to be connected to 0volts.
So I am now measuring the keyboard lines which leave the arrow button for manual jog, as the drive connecting socket not accessible, and is reading 4.8vdc.
When pressing the arrow button the test point voltage comes down to 0.650VAttachment 8763Attachment 8764
And when I keep this button pressed the screen shows the axis coordinates changing.
I must be totally blind I can't see what is going on. I must be real close solving this. Please note that I used a jumper wire to bridge the limit switch computer input to save some time testing limit switches. IF I do not do this the motors de-energize. Should i have done this or not?