Thread: VFD (?) tripping RCD
Threaded View
-
27-11-2011 #14
I would hope so! The IEE recommend (0.1 + cable resistance) ohms earth continuity ,say 0.125 ohms. To get a volt of difference you will need 8 Amps of earth current! If you can, borrow an earth continuity tester and make sure the resistance between parts is less than 0.1 ohm.
Although a potentially unsafe practice this shows no problem. Assuming you are using a digital multimeter as opposed to an old AVO, the input impedance of the meter will be about 10 MΩ. So you are measuring a current of only 18 μA.[*]Measured the voltage above with the spindle running, same result. If I disconnect the earth wire I get 180VAC between frame and earth...so I didn't do that for long!
All VFDs produce high levels of RF. In order to comply with the EMC directive they are fitted with RF filters on the mains input. These have relatively high capacitance to earth which results in a high reactive current to earth and can trip RCDs.something to do with filters in the VFD providing a path to earth - which then trips the RCD
Try measuring the leakage current of the VFD on its own. If that is the problem connect it via a separate, lower sensitivity RCD but make sure your earth bonding is good!
Russell.Last edited by russell; 27-11-2011 at 02:50 PM.
Thread Information
Users Browsing this Thread
There are currently 5 users browsing this thread. (0 members and 5 guests)
Similar Threads
-
VFD Tripping an RCD
By Washout in forum Spindles & Drive MotorsReplies: 13Last Post: 04-09-2017, 02:07 PM -
RCD tripping
By motoxy in forum General ElectronicsReplies: 4Last Post: 23-02-2013, 09:36 PM




Reply With Quote
Bookmarks