Hybrid View
-
08-11-2016 #1
I didn't have much joy using an SSR to switch my toroid supply on. Can't quite remember what it did now but something didn't work. I then read they aren't good with these types of loads. They also fail ON. Swapped it out for branded contactor (controlled by 24V logic on an estop circuit) and it works fine. Thanks to a kind forum member for sending me that part FOC !
Would go the contactor route if I ever built another. The inrush current bothered me but then it not really my area to comment in detail.
The mains switch made me chuckle. Should also be fine but then it's not part of a safety circuit if you want to have that feature in your system
-
08-11-2016 #2
This could be because some SSRs switch only at the nearest zero crossing point, which is the point that gives the highest inrush current for a transformer, so not such a great idea. Other than that I can't think why they wouldn't work well.
I agree neither is going to fair well with any modern safety inspection.
-
09-11-2016 #3
I did look at a peak switching SSR, but after seeing the price, quickly abandoned that idea.
.
I'll probably just go for a contactor. The E-stop relay in this machine did power the original drive power transformer, but it was a 300VA aprox. <mind has gone blank, but square iron/steel type> transformer. So not only was it smaller, it wouldn't have the same power on surge as a toroid.
.
The toroid will be controlled via the E-stop circuit, which runs on 24VDC, but I think it's not that large a supply. I meant to check it's output today, along with the E-stop relay rating but forgot. Last thing I want is it to cause a brownout when the contactor gets powered up, as the 24V also powers various sensors.
However, having just checked the wiring diagram, I could always just use a 230VAC contactor...Avoiding the rubbish customer service from AluminiumWarehouse since July '13.
-
09-11-2016 #4
I'm going to be using a WEG Mini Contactor, CWC16.
16a for £12, my TR is also a 500va
http://chaloncomponents.co.uk/index....actors-7a-16a/
Rectified I'm getting 42v, the drivers are MSD542 x3.Last edited by Lee Roberts; 09-11-2016 at 02:15 PM.
.Me
-
09-11-2016 #5
Those look like useful little devices, Lee, and a good price. One thing that they never seem to tell you, though, is the coil operating current which would be useful for the OP trying to decide if his 24V PSU has the spare capacity to operate it. Personally, assuming that transformer switch-on doesn't trip the supply breakers, I wouldn't bother with a soft-start at these relatively low power levels and just switch directly. Mine seems fine without (650VA toroidal).
Here's a question for the gang, though. Like a lot of small contactors, this is designed to handle 3-phase and therefore has 3 main N/O contacts. If you are using it on single phase, would you just use one contact, wire all three in parallel, or all three in series?
-
09-11-2016 #6
Well I do know the models of a DC flavour have low consumption coils, the idea is you can use them with a PLC directly, no interface relay required.
I probably don't know enough to comment but I would think the coil uses such a small amount it would be negligible?
Catalog: Miniature Contactors CWC
http://www.weg.net/files/products/WE...re-english.pdfLast edited by Lee Roberts; 09-11-2016 at 09:06 PM.
.Me
-
09-11-2016 #7
You have to dig deep in the catalogue to find the numbers, but it looks as if the 24V DC version takes around 150mA. The low-power version is about half that.
-
10-11-2016 #8
Hi
I have had a dig around the WEG site and I saw consumption figures for the CWC16 coil. The C03 coil takes 2.6 to 3.7 Watts and the L03 coil takes 1.7 to 2.7W. 2.7W at 24v is 113 mA, so it shouldnt tax the power supply a great deal.
I have just measured an ABB contactor with a 24v AC coil which gives 5.5ohm - that would be taking about 100w on 24vdc, I don't know what the impedance to 50Hz AC is, but it still seems a hefty whack.
The WEG wee beastie is pricey though in the WEG catalogue - so £12 from Chalon seems a damn good price, especially if you get the L03 coil.
Cheers,
Rob
-
The Following User Says Thank You to cropwell For This Useful Post:
-
09-11-2016 #9
If I understand the question I connected live and neutral (brown and blue) to the contactor so they were both switched. See second photo in post #102. Earth was permanently connected elsewhere. I controlled the switching using 24V DC logic (white wires) from the estop circuit
http://www.mycncuk.com/threads/6988-...cnc_MK3/page11
-
09-11-2016 #10
That's a good answer to a slightly different question! No problem at all with that, if you want to switch neutral as well as live. Perfectly reasonable thing to do. What I was thinking about more, though, was the case where you are just switching live (which is what I do, and leave neutral connected). In this case, you might think of putting the contacts in parallel, to reduce the current through each contact by sharing it across all of them. However, when you switch off (probably worst case for arcing at contacts), inevitably the contacts will open at slightly different times so you will end up with one contact set, the last to open, switching the full current. I have seen suggestions that it is better to wire the contacts in series, which can reduce arcing. Some heavy-duty switchgear works like this, especially if switching DC. Anyway, it's all a bit academic if you are working within the spec of the contactor (or relay), I would hope.
Thread Information
Users Browsing this Thread
There are currently 1 users browsing this thread. (0 members and 1 guests)
Similar Threads
-
Toroid transformer no ouput
By eurikain in forum Electronic Project BuildingReplies: 40Last Post: 16-12-2015, 03:54 PM -
Smoked a contactor , but why?
By Poshpaws in forum Gantry/Router Machines & BuildingReplies: 8Last Post: 27-03-2015, 09:42 PM -
retrofit Boxford vmc mill 260 Info needed on Yaskawa contactor relay and VFD choices
By Roboteernat in forum Boxford Vertical MillsReplies: 10Last Post: 13-03-2015, 12:25 PM -
Relay V Contactor
By GTJim in forum General ElectronicsReplies: 9Last Post: 18-03-2014, 10:10 AM -
Contactor sizing?
By Swarfing in forum General ElectronicsReplies: 5Last Post: 27-12-2010, 08:58 PM
Bookmarks